I'm unaware of ANY recent HVAC equipment whose motors couldn't tolerate 200-230 nominal, delivered voltages.

More current will be drawn at the reduced voltage.

The big issue for many HVAC systems is not the motor -- but the control power transformer.

Many are multi-tap -- in which case re-tapping would be most wise.

Unlike the motor, the control logic is pretty finely dialed in.


Tesla