You need to get in touch with either PG&E -- their Green Book --- or SMUD or Roseville Electric.

All are EUSERC conforming utilities.

ONLY EUSERC approved equipment will be tolerated.

You need to touch base with the Poco -- the AHJ is almost irrelevant.

A 5 pack would permit you to power up a 'house panel.' -- I.e. Landlord's panel.

It's a loser as far as the Poco goes.

You've been talking to the wrong guy. -- You HAVE to get in touch with the Poco.

You can meet every AHJ issue -- and then fail your Poco standards -- and never get any power.

The Poco does not take orders from the AHJ, period.

Go to the EUSERC site -- Bing is your friend.