A little further on this.
(C) Conduit Bodies.
(1) General. Conduit bodies enclosing 6 AWG conductors
or smaller, other than short-radius conduit bodies as described
in 314.16(C)(2), shall have a cross-sectional area
not less than twice the cross-sectional area of the largest
conduit or tubing to which they can be attached. The maximum
number of conductors permitted shall be the maximum
number permitted by Table 1 of Chapter 9 for the
conduit or tubing to which it is attached.
(2) With Splices, Taps, or Devices. Only those conduit
bodies that are durably and legibly marked by the manufacturer
with their volume shall be permitted to contain
splices, taps, or devices. The maximum number of conductors
shall be calculated in accordance with 314.16(B). Conduit
bodies shall be supported in a rigid and secure manner
314.16 (b) table requires 5 CI for each #6, & 2.5 CIfor the #10
Sounds like 38.5CI .
Using Red Dot mfg data, you will need a 2" LB/LL/LR for your conductors.
Last edited by HotLine1; 07/30/11 12:46 AM. Reason: typo