CEC 12-610 (1) ".....bushings of insulating material or equivalent devices." But consider subrule (3) which requires the protection to be visible for inspection when cable is installed in connector or clamp. So as long as the electrical tape is installed with that in mind it should be okay. Anti-shorts are preferred because they are quicker, easy to see and more reliable.