Expanding on Yoopersup's post above:

Finding Full-Load Amperes from a given Apparent Power Value - i.e.: "Volt Amps"...

Abbreviations Used:

a: "VA" = Volt Amps
... VA = Apparent Power

b: "KVA" = Kilo Volt Amps (1,000 Volt Amps)
... KVA = VA × 0.001

c: "FLA" = Full Load Amperes

d: "E-pri" = Primary Voltage

e: "E-sec" = Secondary Voltage

f: E-adj" = Adjusted Voltage

g: "3ph" = 3 Phase

h: "1ph" = Single Phase

i: "2W" = 2 Wire

j: "3W" = 3 Wire

k: "4W" = 4 Wire

l: "L-N" = Line-To-Neutral (Phase Line to Grounded Conductor)

m: "L-L" = Line-To-Line (Phase Line to Phase Line)

n: "Sq. Rt." = Square Root

o: "×" = Multiplication Symbol

p: "÷" = Division Symbol

________________________________________________________________________________________________________________________

Transformer = 45 KVA
E-pri = 480V; 3ph 3W
E-sec = 208Y/120V; 3ph 4W

Steps to perform:

  1. Obtain VA rating from KVA..
    45 KVA x 1,000 = 45,000 VA.
  2. Obtain "Adjusted Voltage Value"..
    a: If Transformer is Single Phase, no adjustments to Voltage Value is necessary,
    b: If Transformer is 3 Phase, multiply the Rated Voltage by 1.732 (Sq. Rt. of 3).
  3. Divide the Rated VA value by the Adjusted Voltage Value. This result is the Rated FLA Value...
    ... VA ÷ E-adj = FLA


Example #1:

Find Primary FLA for the 45 KVA 3ph Transformer...

1: 45 KVA × 1,000 = 45,000 VA.

2: E-pri L-L = 480V; 3ph
480 × 1.732 = 831.36 (round off to 831)

3: 45,000 VA ÷ 831 = 54.15 Amps

Primary FLA = 54.1 Amps.

-------------------------------------------------------

Example #2:

Find Secondary FLA for the 45 KVA 3ph Transformer...

1: 45 KVA × 1,000 = 45,000 VA.

2: E-sec L-L = 208V; 3ph
208 × 1.732 = 360.26 (round off to 360)

3: 45,000 VA ÷ 360 = 125.00 Amps

Secondary FLA = 125.00 Amps.

-------------------------------------------------------

Example #3:

Find Secondary L-N FLA for the 45 KVA 3ph Transformer...

1: 45 KVA × 1,000 = 45,000 VA.

2: 45,000 VA ÷ 3 = 15,000 VA

3: E-sec L-N = 120V; 1ph
120 × 1.00 = 120 (no E-adj necessary for 1ph).

4: 15,000 VA ÷ 120 = 125.00 Amps

Secondary L-N FLA = 125.00 Amps.

-------------------------------------------------------

Example #4:

Find Primary & Secondary FLA for a 50 KVA 1ph Transformer...

E-pri = 480V 1ph 2W
E-sec = 120/240V 1ph 3W

1: 50 KVA × 1,000 = 50,000 VA.

2: E-pri L-L = 480V; 1ph
480 × 1.00 = 480

3: 50,000 VA ÷ 480 = 104.167 Amps (round off to 104)

Primary FLA = 104.00 Amps.

4: E-sec L-L = 240V; 1ph
240 × 1.00 = 240

5: 50,000 VA ÷ 240 = 208.334 Amps (round off to 208)

Secondary L-L FLA = 208.00 Amps.

-------------------------------------------------------

The following NEC Articles shall be referenced for Transformer Installations:

a: Article 240 (Overcurrent Protection),

b: Article 250 (Grounding and Bonding),

c: Article 408 (Switchboards and Panelboards),

d: Article 450 (Transformers and Transformer Vaults).

Hope this information is helpful.

-- Scott


Scott " 35 " Thompson
Just Say NO To Green Eggs And Ham!