We recently investigated a full blown hospital with a 4000 amp 480 service with six 800 amp disconnects and no main. The plan was to put in a 1200 amp PV disconnect on the common 4000 amp bus, the local AHJ approved this per 230.2 and 230.71.
The project was scrapped for financial reasons, but may be restarted if they can incorporate the work into a future expansion project.
I have never seen the six handle rule applied to such a large service.