This Device _APPEARS AS_ a Power Monitor, for logging a Single Phase Circuit over a given Time Period.

Input #1 would be the Current Probe Input, via a Clamp-On type Ammeter (Current Transformer type Current Probe).
Connect a compatible CT to the "CH-1" Input on the Meter.
Set the Parameters for CH-1, per the specifications of the Current Probe used.
Clamp the CT around ONE Conductor on the Circuit to be Monitored.

Input #2 would be the Voltage Probe Input.
This may be via:
1: Voltage Probe Leads of the Current Probe,
or
2: a Pair of Alligator Clipped Voltage Leads, connected to the Two Wires of the Monitored Circuit, at a Termination Point (so as to measure the Circuit's Voltage).

The Multiplier settings for CH-2 _MIGHT BE_ as follows:

A: Using the Current/Voltage Probe: 100:1,
B: Using Alligator Clip Leads: 1:1

These figures are not device specific, so best to verify prior to actual use.

Do a Google Search for your Model Number. This might yield more information than what is found in the Document you have now.

Good luck... sorry I could not give you actual answers! frown

--Scott


Scott " 35 " Thompson
Just Say NO To Green Eggs And Ham!