Unless you are running full size conductors to both structures I do not think you can do what you propose. If you are running conductors for 200A to each structure you will need OCPD of 200 amp at the pole after the meter. You are over the length of the "tap rule"
You would need to bond at the pole and run 4 conductors to each structure.