client has 6 recessed cans with two three ways controlling them. He has the BR30 type fluorescent bulbs in each of the cans. The problem is when the switch is OFF the bulbs flicker.

Here is the items that i have checked in the device box. (No neutral available in the device box)
>Voltage to grounding with the lights ON 119V
>voltage to grounding with the lights OFF 23V
>The 23V disappears as soon as i connect a resistive load (obvious Phantom voltage)
>NO dimmer connected
> client has already replaced the switches with new ones.

The existing CFLs are about 1 year old so I asked the customer to change the bulbs with new CFLs and see if the flickering goes away.

What could be causing the flickering on the CFLs