Up2code;

If you utilize the same Circuits that were used to run the original 400W MH Fixtures, you should not have any issues from "possible Triplen Harmonic Currents" in the Common Grounded Conductor of 4 Wire Multiwire Circuits.

Since the new Fixtures will draw apx. 40% less Volt-Amps than the original Metal Halide Fixtures, the Circuitry will also be reduced apx. 40% of the original Amperes.

Most - if not all, of the commonly used "Brand-Name" Electronic Ballasts, have a THD of 10% maximum.
That's about the same as an HID's Constant Wattage Autotransformer (CWA), High Reactance-High Power Factor (HX-HPF) or Regulated Lag (Reg. Lag) Ballast.

*** Installation Note - per 4 Wire Multiwire Circuitry & Triplen Harmonics ***

If the L-N Loads are kept to a "Design Limit" of 10 Amps, even with a THD of 33.333%, the absolute maximum Current that could possibly flow on the Common Grounded Conductor of a 4 Wire Circuit would be 30 Amps.

In reality, the Harmonic stories have been grossly exaggerated.

It is true that Harmonic Currents will exist and flow in ANY AC System which drives Reactive Loads.
These Currents "Reflect" back from the load, and "against" the Transformer feeding that load.

Harmonics exist in 2 Wire Circuits and 3 Phase 3 Wire Circuits, where Reactive Loads are driven; however, there is no "Triplen" scenario involved.

Harmonics also exist in Single Phase 3 Wire Systems, where Reactive Loads are driven; however, as with the 2 wire Circuits and the 3 Phase 3 Wire Circuits above, there is no "Triplen" scenario to deal with.

3 Phase 4 Wire Wye Systems have the "Triple-N" (Triplen) scenario, which is the relevant issue of design - and what you're concerns are pertaining towards.

Don (Resqcapt) made a very good statement:
"If the manufacturers of a certain piece of Equipment design it to be extremely noisy (reflect THD >30%), then that manufacturer should be responsible for "cleaning" the AC input outside of the Load's input"

Simply this means that the THD on the Line input of a piece of Equipment should not be higher than 10% at any Harmonic point(s).
Even 10% seems somewhat excessive to me, as there are methods of reducing the Distortion (noise) being reflected back from a given Load, to a level lower than 10%.

If you believe there may be an excessive THD issue, see if you could obtain the listed THD of the Ballast used.

Typical "Electronic" Instant Start Ballasts, for 6 F32T8 Lamps (265ma Lamps), will be listed as <10% THD.
Refer to the Fixture catalog for THD quoted values, or request the THD value(s) from whomever is quoting the Lighting Package.

Good luck with your project.

Feel free to post again if you have further questions, or any information towards the possible THD listed on the proposed new Ballasts.