2005 NEC 240(F)...

TRANSFORMER SECONDARY CONDUCTORS:

Single-phase (other than 2-wire) and multi-phase (other than delta-delta, 3-wire) transformer secondary conductors shall not be considered to be protected by the primary over-current device.....

This phrase has been in the Code for years -- for the reasons detailed above.


Tesla