Originally Posted by waymag
Not one GFCI. That is the problem I am having. Is it just sitting on the floor??? What is wrong with these folks?


I can think of no requirement for GFI protection based on the NEC. This is not a construction site, so Article 590 does not require GFI protection. Judging by the enclosures, this is an indoor installation, so the requirements in 210.8(B) (4) do not apply either.