The transformer is protected under article 450.3. If the primary disconnect is sized at not more than 125% of the primary FLA, a single disconnect is not required on the secondary.

The secondary conductors are protected by the tap rules in 240.21(C). There are situations where a set of tap conductors can feed multiple devices.