I know the drive manufacturers and wire manufacturers are making a killing on these new output cables. I am sure they work very well. But, I have installed and repaired hundreds of VFD's in my career. THHN with line and load reactors always did the trick for me. You really do not need the load reactor unless the distance from the drive to the motor is very long. Like over 100'.
Never mix line and load conductors in the same raceway. Always run control logic cables separately in there own raceway. Always program the carrier frequency as low as possible. Buy quality drives. Price is not always the indicator.