IMHO sizing the genny for 200A is a total waste of money. In an emergency situation you should not need more than 50A at most for a 2200 sq ft house with gas heat. We live in a rural area (frequent power outages) and have a PTO 13.5kW generator that is cord connected to an whole-house inlet. That inlet back feeds a mechanical transfer CB (50A) and main switch inter-lock in position 2 on the main panel. In this manner we can operate any circuit we need without having to define it beforehand. We have enough power to operate the house plus one "big" appliance and I just dont try to run the dryer and the oven at the same time. General house load is 20A on each line. Remnants of hurricane Ike saw it getting 16h of use a day for 6 days without a hitch. Costs of generators above 12-13kW start getting up-there. The cost of the interlock (Square-D) and 50A CB was less than $50 3 years ago and beat the pants off related charges for any transfer switch system with pre-defined "critical" circuits, not to mention the simplicity of installation. I have yet to trip the breaker but a 50A at the panel and a 50A pop out breaker on the genny should prevent an undervoltage situation. I also had hubby wire up a frequency meter that plugs (two separate cords and caps) into two outlets (supplied by L1 and L2) that I identified and the display scrolls through voltage, frequency and rpm so we can keep an eye on the genny performance under different loads from in the house. The idiot gauge on the PTO generator is HOPELESS, and we use frequency to set the throttle on the tractor. I am very happy with the set-up and it was modestly priced for what we can do with it. Sure a auto-transfer and start would be nice but we would never get the utility out of it for what those units cost. Thats my 0.02.