FYI- The install went well with no defects.

Another question for Mikesh or anybody else who wants to chime in.
In both the CEC and OESC, rule 28-210 states that instantaneous-trip circuit breakers shall not be used unless part of a combination starter, etc.
So with this install, where the motor has thermal protection and a FLA of 15amps, if it was fed through a regular breaker box, could you protect it with say a 30A circuit breaker (non-time delay) and feed the motor directly with #12 wire?

Thanks... Bruce