That's the basic scenario here in NJ, probably the same in Ma.

800 amps is max OH (from pole mtd pots), larger is pad mount xfr. PSE&G area, layout tech determines locations; EC responsible for pad sub-base; EC installs primary conduit(s)from pad to PSE&G designated location (to PSE&G specs). PSE&G installs and terminates primaries. EC is responsible for all secondary work. CT's & meter pan are supplied by PSE&G; PSE&G wires CT's and meter. All is done to PSE&G Green Book 2005 with amendments (3).

The Green Book, and amendments is available on the internet at PSE&G website.