Originally Posted by Tripp
Thanks for the quick reply. But still I have these concerns: NEC 250.146(D) "Isolated Receptacles" requires "an insulated equipment grounding conductor" which I won't have with 12-2 romex since the copper is bare. The same article requires that this isolated ground terminate only at the service, i.e., not in the branch circuit distribution panel. Further thoughts?


Use MC