I agree with John, the 250.66 requirement for connection to water pipe is a remnant of the days when water supply lines were metal and that was your best ground electrode. Now days the plumbing lateral into a building will generally be PVC and the only real grounding will happen with the inadvertent connection to building steel via the pipe supports.


Greg Fretwell