Sparky- I would agree with your comment that GFCI protection is not required for Brandon's installation. The code reference would be 210.8(A)(2) Exception 2 to (2) 2005 NEC. I would also add that the electric fence should not trip the GFCI no more than a bug zapper would. If it trips the GFCI there is something wrong with the electric fence equipment.


George Little