Originally Posted by gfretwell
Wait, WHAT? The neutral bar in the gutter makes sense, but I really disagree with separately bonding the neuetral bars in the panels to the enclosure. Neutral current flowing through the enclosures and conduit is completely unsat.

250.24(C) is pretty clear that this is the way NFPA wants to see it, though. The only exception is if all the service disconnects are in the same enclosure.

FYI, NEC 2008 handbook retains gec_tap2.jpg, but does not include gex_tap.jpg.