That is correct. with that many wires bundled, derating is in order. (310.15(B)(2)). I also see a possible issue with the three gang switch box and wire fill.

All that time and effort the installer (not a sparkie) took in cut the chases in the wall plates. I typically punch a series of holes with a 5/8 of 3/4 inch bit and put a nailer between the studs. This will prevent me from bundling and makes for a clean installation. With the 4 holes he drilled to on the corners may have been enough for the wires in some of the pics. Sloppy, sloppy, sloppy.

I wonder the yahoo who pulled the wire gets paid by the foot?

Last edited by sparkyinak; 04/06/08 02:21 PM.

"Live Awesome!" - Kevin Carosa