Both Transformers feed the Same Building,
(Sorry George 240.92 (B) (2) 2
Allowes six disconnect Switches per set of Conductors if a Supervised Industrial Installation.
Also 240.30 (B) Have Several Exceptions to the one disconnect Rule .225.33 Maxium # of disconnects says six for EACH suppy!So could you have four feeders , They say PER SUPPLY , here we would have several supplys Right
Reason not to have single disconnect Switch you ask. COST Ground Fault Protection. any breaker over 1000 amps on a Wye Requires it. If you can get your breakers under 1000 amps its not required.