The method posted by OUSoonerFan3 is what you were looking for - regarding the "Mathematical Way".
If you are good with Math, this will work great for 3 Phase "L-R" Circuitry (Circuitry in Panelboards, with Circuits on the "Left" and the "Right" sides).

It doesn't work with the following configurations:
  • Single Phase "L-R" Panels,
  • Panels / Gear with only a "Single Row" of Circuitry,
  • Power Panelboards with multipole Circuitry under the same "Number" - such as a 3 pole OCPD at the upper left of a Panelboard identifies A, B and C as "Circuit 1",
  • Panelboards with "Stack Breakers" or "Piggyback Breakers" - such as a "QO-20/20",
  • Old "Bulldog" / "Pushmatic" Panels


Iwire's response brings up a very good point - create color charts for various scenarios.

I have created a set of these in Excel, which you may use if needed.
Just E-amil me, and I will bounce it your way.

Scott


Scott " 35 " Thompson
Just Say NO To Green Eggs And Ham!