If the are asking for a load calculation this is what they are probably looking for:

1) General Illumination, 220-16 (b) @ 125%
2) General Purpose Receptacles, 220-44, Table 220-44, and 220-14 (a) which ever is greater. First 10KVA @ 100%, the remainder @ 50%.
3) Water Heaters 422-13 @ 125%
4) Out Side Lighting 210-19 (a)(1) @ 125%
5) Heat 220-51 Non-coincidental Loads 220-60 @ 100%
6) Motor Loads 220-50 (List every single motor out) @ 100%
7) Sign Circuit 600-5a, and 220-14 (f) @125%
8) 25% of the Largest Motor Load, Sec. 460-24 & 220-18 (a)

That is it, sharpen your pencil, get your notebook out and walk the plant and collect all that data, and list it out in excel.