130-150' home run is poor design.

But a 20' square room on a single circuit will almost certainly have the last recept 100' from the breaker. 6% voltage drop at breaker rating.

But breaker rating or even 80% of breaker rating is much more than a residential circuit will see in most cases.

Up sizing wire is not going to solve a voltage drop problem, but the problem almost never really exists.