Doesn't this fall in the Scope for the Utility Company's Design Engineers to specify?

If YES, then submit the standard items to the Utility Design Engineer:
  • Load Calcs,
  • A site drawing (building footprint),
  • A summary of conditions / scope,
  • Cutsheets / specs for the new Service Equipment to be installed,
  • Filled out Service Planning application form(s),
  • Application(s) for Permit(s),
  • Necessary Fees.


If NO, then you will be the responsible party for compiling the Service Feeders' Design; and so begins the questions list:

  1. What is the Calculated Load?
  2. Will all Parallel Conductors share a single Duct, or will there be Parallel Ducts with Four Feeder Conductors in each?
  3. Will you use Copper or Aluminum Conductors?
  4. Do you need to adjust size, due to Voltage Drop issues?
  5. Is there any requirements from the DBS or Utility for a minimum Conductor size, &/or Conductor material + insulation?
  6. Were the "Original" Service Entrance Feeders + Ducts installed by an EC or the Utility Dept.?
  7. Any ideas of the "Original" Load Calcs' figures, which determined the size of the "Original" Feeders?


Out of curiosity, what size Transformer is used (75 KVA - 208Y/120VAC or 175 KVA, 480Y/277VAC), and is the Service Capacity 400 Amps?