Bah... It looks like you do use the fuse.

Largest motor X 300% (non-time delay. 430.52)
=224.4A

Now add the remaining.
224.4
74.8
46.2
+16.7
= 362.1, round down and you get a 350A feeder fuse.

I tried to figure this out for an hour last night with no luck... I come back and put 15 minutes into it this morning and get it. new day new ideas I guess.


Shake n Bake