Originally Posted by kyelectric
Just wondering. When I measure the voltage in a panel across the line conductors I read 218 on my voltmeter. Is that a low reading on a 240 volt system or a high reading on a 120 - 208 system? From one leg to neutral I read 125 volts.


If all 3 L-L voltages are the same and all 3 L-N voltages are also the same then you have a 208Y/120 system with above normal voltage.