Originally Posted by gfretwell
If your equipment is tight I doubt you will leak enough to trip the GFCI.


I am not sure you understood what I was trying to say.

I was not talking about water leakage.

Almost all utilization equipment has some current leakage, the more equipment connected to a GFCI the less 'headroom' that is left between O ma and the trip level of the GFCI.

Of course your right it may work fine, on the other hand it may cause nuisance tripping of the feeder, which if I am hired to do a job I want to try hard to prevent.

As much as I advocate the use of GFCIs I think using GFCI mains to accomplish this is a poor design.

If I have the choice I install GFCI receptacles at each point of use and would only connect one hardwired device to each GFCI unit.





Bob Badger
Construction & Maintenance Electrician
Massachusetts