Mike, I was actually taught that the Romexes had to be separated in order to provide for heat dissipation by a Riverside County inspector. Have you had any inspections yet? (I also cut all the ty-raps off of the wiring inside panels when I find them. They make for a very neat looking job, but when they're all bundled for 24" or more, as mentioned earlier, it becomes a derating problem)