Aussie240 is right. MCBs have only a fraction of the switching endurance of a light switch.
MCBs are only required by AS/NZS approvals testing to perform 1000 switching operations at full load, whereas light switches are required to do tens of thousands.
MCBs were never intended for control of a load, only isolation for servicing and overcurrent disconnection.