It is most likely the power factor correction that is giving your contactors such a hard time. Depending on whereabouts in the mains cycle the contactor closes, PFCs can and do generate savage inrush transients that chew contactor contacts. Contactor manufacturers are aware of this, and do publish tables giving the derating factors for different combinations of contactor and lights. I advise you to seek the wisdom of your contactor manufacturer.