So, then I should open all of the 1/4" KO's to allow for weeping of the condensation?

Thanks for the concise answer, Joe, and GWZ, thank you as well for your input.

My synopsis: since there's no listed connector for bare solid copper #6 or #4 wire without armor, then a raceway must be used.

The weep holes (if that is what they indeed are) need to be opened to allow drainage, but somehow must also comply with 110.12(A)...

Does this sound reasonable?