WFO: we had that happen once a couple years ago on a 480V plant- breakers tripping left and right, popping like popcorn! Was bad news. Turns out, the contractor, despite reassuring us TWICE that he had metered and verified rotation, had indeed swapped phases at the UPS bypass switch. The only good news was it wasn't my fault, nor my problem, as I didn't work there yet. But oh, I hear about it every time anyone suggests an online test vice scheduling an outage...