"Is this just the three phases of 208Y/120 V brought in without the neutral?"

That would be the result; 208v line-to-line.


"Would this be considered an isolation transformer?"

More likely a neutral-deriving device. Here's why I say that: (208/220)*127 = 120

It seems that the function of this transformer is to restore a "lost" neutral, or perhaps a way to provide an isolated (floating) neutral.


Larry Fine
Fine Electric Co.