When you disconect the neutral and the circuit is closed by any conected load (like a light bulb, for example) you read the hot wire voltage in the neutral. There is no current flowing through the circuit, so there is no voltage drop in the load.
From your words, everything looks fine to me.
The staple was never the problem, so the reading didn't change after you removed it.
Connect the neutral again and test, you'll see.

Joe.-