Bjarney has covered it very well!

Just for the sake of redundancy, I'll add some "Simple Stuff":

The Open Delta bank is able to deliver 86.6% of the KVA into 3 Phase loads.

Example: If one pot is 6 KVA and the other is 4 KVA, the output KVA is 8.66 KVA - not 10 KVA. See Bjarney's descriptions and formulas above.

If an existing Closed Delta network (three Pots connected together in a parallel / delta scheme), and one pot fails, the remaining two pots can continue to deliver 3 phase 3 wire AC - but the maximum output KVA is only 58% of the original KVA rating.

Example: 3 - 10 KVA pots connected in a delta scheme has an output power of 30 KVA max.
One pot fails, due to a secondary coil becoming barbequed.
Network can continue to deliver 3 phase 3 wire power, with a maximum of 17.4 KVA apparent power output - as opposed to the original 30 KVA of apparent power available.

The normal rating of a 3 Phase 4 Wire Closed Delta will have a center pot which is at least 200% larger than a single "Outer" pot.

Example: a 45 KVA 3 Phase 4 Wire Closed Delta would have a center pot rated at 25 KVA, and the two "Outer" pots rated at 10 KVA each.

Open Deltas are similar for 4 wire applications, but the "Single Phase" pot might be as large as 400% of the "Kicker" pot. All depends on the calculated loads to be driven.

For 3 Phase 3 Wire settings, the pots are typically sized equally - on both Open and Closed Delta networks.

Scott s.e.t.

P.S. The term "Pot" is referring to a Single Transformer - or more precisely a "Stand-Alone" single phase Transformer.

Bjarney's examples and formulas are much better than my stuff! I'll need to add this to the tech reference section!

S.E.T.


Scott " 35 " Thompson
Just Say NO To Green Eggs And Ham!