The 14KAIC CB's are not fully rated, because they are not rated higher than the available fault current of 30KA by themselves. If the CB's rated @ 14KAIC are not series rated with the upstream fuses (from your example) then you have a code violation. No labeling in the world will help if there is no fully rated device or series rated combination at the panel (with 30KA available). The only agency that determines a series rated combination is UL and it would be in the associated literature with the device(s).

[This message has been edited by Ron (edited 05-19-2002).]


Ron