I too suspect that Kaos was involved with some level of design here, as it's operation is inverted [can't hear conversation inside but if your outside it's clear as a bell].
Plans most likely have Siegfried's PE stamp on them
Having the split coils connected in parallel on this arrangement produces 120 VAC in that coil. Connecting all three individual transformers in a Wye configuration where the voltage of each transformer is 120 VAC will produce 208 VAC L-L / L-L-L, or 120 VAC to the common - this is the common method of creating a 208Y/120 VAC 3 phase 4 wire Wye system when using 3 common type 1 phase 120/240 VAC split coil transformers [Utility Companies' pole mounted xformer banks].
If the split coils were connected in series additive, the voltage of each transformer will be 240 VAC.
Now if we connect the 3 individual transformers in a Wye configuration where the voltage of each transformer is 240 VAC, the L-L / L-L-L voltage will now be 416 VAC, and of course the voltage from any one of the three transformers to the common will be 240 VAC.
This would be a 416Y/240 VAC 3 phase 4 wire Wye system.
If the common is not used, then the system would just be a 416VAC 3 phase 3 wire Wye.
BTW: Can you see how the pictorial "Y" schematic is made up of 3 individual transformers?? That's why I wanted to have the pictorial schematic drawn above the 1 line schematic - so there's a visual relationship to use.
Scott SET