Shock, and all, NEC 334.15(C) In Unfinished Basements. Where cable is run at angles with joist in ubfinished basements , ...2 #6 or 3 #8 directly to lower edge.... Smaller cables SHALL be run either through bored holes in joist or on running boards. Below the joist NM cable is a violation. It isn't just support but, protection. People used to use the wires as clothes line and hang wet clothes from wire hangers from the conductors. A real treat when they had K&T wiring. Alan--