I do not want to seem critical here however do I see all the branch neutrals leaving the panel near the top and all the branch hots leaving from the bottom?
This can / will cause the metal enclosure of the panel itself to get warm or hot depending on the load carried by those conductors.
It is also a violation of 300.3(B).
Bob Badger Construction & Maintenance Electrician Massachusetts