the red (actually orange) tag is the Teleco ground wire identifier.
The service Duplex) enters into the far left panel then splits to the middle panel. The "plumbed in" panel is supposed to be a sub-panel, however, the #6 conductors to the main pullout were tapped under the terminal screws on the main of the middle panel.
The zip cord was an extension cord that the homeowner used to plug in at the top of the stairs. It was connected to a "painters light." Reason: the basement light switch was broken.
The other concern is the clearance here. The two far panels are blocked by the washing machine.
We relocated service to provide required clearance. We installed 2-100Amp CB panels and got rid of the fuse boxes.