The SE cable can not be used here. But the distance is well within what would be allowed here in SF.

It's just one of those regional things...

Heres some 2002 commentary on the subject of 230.70
Quote
No maximum distance is specified from the point of entrance of service conductors to a readily accessible location for the installation of a service disconnecting means. The authority enforcing this Code has the responsibility for, and is charged with, making the decision as to how far inside the building the service-entrance conductors are allowed to travel to the main disconnecting means. The length of service-entrance conductors should be kept to a minimum inside buildings, because power utilities provide limited overcurrent protection and, in the event of a fault, the service conductors could ignite nearby combustible materials.
Some local jurisdictions have ordinances that allow service-entrance conductors to run within the building up to a specified length to terminate at the disconnecting means. The authority having jurisdiction may permit service conductors to bypass fuel storage tanks or gas meters and the like, permitting the service disconnecting means to be located in a readily accessible location. However, if the authority judges the distance as being excessive, the disconnecting means may be required to be located on the outside of the building or near the building at a readily accessible location that is not necessarily nearest the point of entrance of the conductors.

Heres a little photo gallery of Service conductors that travel within walls from the last time this came up. (Interpeting the same code) http://www.markhellerelectric.com/services/serviceconds.htm



[This message has been edited by e57 (edited 02-07-2005).]


Mark Heller
"Well - I oughta....." -Jackie Gleason