While troubleshooting an open ground condition on a circuit in my home, I looked in my panel for the first time...jaw hits floor.

Dorbell transformer inside panel (at bottom)
1 pri lead from x-former wrapped around a wire at breaker, other lead wire-nutted to one of the ground wires sticking out of wire bug
Nothing about this panel very neat or workmanlike
Black friction tape on service neutral
Many grounds too short to reach GND/Neut bar, all wire-bugged to #10 GND of dryer cable
Too much outer jacket insulation on main cable, leads too long
30A dp breaker for hot water tank, using 12-2 w/ gnd wire
Panel not clearly or properly labeled
Master bedroom, livingroom, bathroom, and 1 duplex receptacle in small bedroom all on one circuit (20A) with all 15A receptacles, 15 of them
No separate lighting circuits
White "hot" lead for hot water tank not re-identified
One strand of grounding electrode conductor peeled back and wrapped around other strands (couldn't fit all of them in the hole?)
Front porch light and rest of small bedroom receptacles on same circuit (at opposite ends of house)