If this installation was 480V, how was the 120V contactor coil powered? With one side connected to ground thru the greenfield, it would still see 277V from any of the 3 phases, assuming a wye system. Was there a separate source of control power from somewhere? Is that what the red wire does for a living?

At any rate, a nasty looking install....