Eandrew If there are any 3way switches on the lighting circuit, the use of a different circuits grounded conductor could be the cause. I have seen two breakers trip because the grounded conductor of a different circuit was used to eliminate the need to run one along with the travelers from 3ways. When this is done a short to ground will trip two breakers. It also makes it tough to put a ground fault receptacle in either circuit.