Shame on everyone involved. The installer failed to bond the cabinet & the conduit nipples (they might be bonded at the other end, though I tend to doubt it). If this passed inspection, the inspector was asleep & if it was energized by the power company, they too dropped the ball.
250-92 is clear about what is to be bonded & 250-94 tells you what you can/cannot use. Plain jane locknuts certainly don't cut the mustard & the #2 jumper from the grounded conductor to the CT cabinet is also missing. Also, the wireway in the upper right corner must also be bonded (bet it isn't).