A call this morning- the lights and ceiling fan went out when they plugged in the vacuum. Hmm...breakers aren't tripped. Pull the cover off the little panel and...

[Linked Image]

Better fix that before I do anything.


[Linked Image]

I changed things around, added some breakers and... Oh well, not very pretty, but it's better, anyhow.
Now to check out that other problem.
*********************************************


[Linked Image]

Easy to trace visible wiring method.


[Linked Image]

OK, let's see, here's the UF coming from the fan.....


[Linked Image]

Better not hit my head on the A/C wiring


[Linked Image]

Guess I better disconnect that A/C


[Linked Image]

Huh, had to shut off 3 breakers to get this box dead, but it's not THIS neutral connection.
*********************************************

Found it! Neutral's loose in same box that they had the parallel 40Amp #14 and 30Amp #12 tied together in. It's my lucky day!