Handle ties are not intented to provide a common trip. They are only intended to provide a common disconnect. The code code permits "approved" handle ties in 240.20(B), but I doubt that the AHJ has approved the wire as a handle tie. Even the handle ties from the breaker manufacturer do not turn 2 breakers into a "common trip" breaker.
Don